Temp drifting on marine air system

Post
Member

tnsailorguy

posts 11

11:21 am January 7, 2012

I have 1992 Sea Ray Sundancer on the Tennessee River. It is a marine air system self contained I think. Unit is located under setee. Last nite I woke up cold and noticed that the temp read 58degrees on my digital control and the unit was blowing cool air. I attempted to adjust thmostat to no avail. Checked connections all seemed ok. The compressed would cut on but no warm air from output. I replaced the short fuse, I think it said it was for reverse cycle. I had let it set 15 minutes while I went to ship store to get fuse. They only had a 4 amp instead of the 5 so I tried it anyway since it was lower I figured . I then turned on the unit and it began to emit warm air. After a few minutes the compressor was warm to the touch but not hot as it had been before. Watched it for a bit and I noticed it would cycle but the readout on the control unit seemed to drift up and down. From lower 60 to upper 70. The temp outside was 48. I shut unit down and came home to find info. I am returning later today. Any imput or things to check would be helpful.

Admin

Steve Pooler

posts 1127

11:43 am January 7, 2012

Before I could help in any way…I need to know exactly what you have for equipment & control…

There can be many differences from brand to brand & even models & models/brands of controls.

I also need to know the temp of the water the boat is sitting in & if you have "Full" flow overboard.

 

Sorry…But with all the variables…I'd just be guessing without that info…  Wink

 

Steve~

Member

tnsailorguy

posts 11

12:03 pm January 7, 2012

I wrote down some numbers from the bottom of the info panel 204 3001 followed by what looked like a zero that had been filled in and a zero with a line in it then in the next box a 2-13315. It is a Marine Air Systems unit. There was water flow about the same as usual shooting maybe three inches from thru hull. I would have to estimate the water temp at around 45 degrees. If you will let me know what and where to look for the specific info you would need let me know and I can get it when I go back to boat this afternoon.

Admin

Steve Pooler

posts 1127

12:36 pm January 7, 2012

Ok if you are sure it's Marine Airrr & not Cruisair that helps a bit…But those numbers I don't recognize… 

A model number off the unit itself would help but also take a look at this PDF http://marine-ac.com/marine-ac…..ion-units/

Scroll thru the pages & find the control & matching board that most looks like what you have…Open the electrical box on the for the unit to see the board…And look for the Penguin on the control…Small Penguin, Big Penguin, Facing Left, Facing Right, or No Penguin at all…

Also know that you cannot run Reverse Cycle heat in water temps 40 degrees or below…Though it may heat a bit you are running a huge risk of rupturing the water coil (with it icing up) & ruining the complete unit…

Sorry that you may have to go to the boat first…

 

Steve~!

Member

tnsailorguy

posts 11

1:24 pm January 7, 2012

Thanks I will get info from boat and accurate water temp.

Member

tnsailorguy

posts 11

2:54 pm January 7, 2012

It is the ECU Display 1992

Member

tnsailorguy

posts 11

5:08 pm January 7, 2012

Changer to correct fuse. It has stopped readout movin up and down. Seems be cycling a lot. Small penguin facing away from logo. Says environmental control unit at top of control. Water temp 49 degrees

Member

tnsailorguy

posts 11

5:10 pm January 7, 2012

About five degrees above what digital thermo says on table. Short cycles outside temp 55 degrees.

Admin

Steve Pooler

posts 1127

5:52 pm January 7, 2012

Ok…That all helps…Thanks Cool

Since that is a ECU control that does not have a temp sensor in the display (like later Passports)

I would locate the temp sensor end & make sure you have not developed a duct leak that is allowing discharge air to blow or leak onto the sensor….This will cause it to short cycle because with the unit running warms the air & it will see that…Then when it shuts it off it sees the air cool quickly & thinks it needs to turn back on…

Another reason to short cycle is the high pressure switch cutting it off & back on…This can happen for the same reason…Hot air leaking out of the discharge duct back into the return air, thus causing the unit to run high pressure…

 

Steve~

Member

tnsailorguy

posts 11

3:35 pm January 8, 2012

Thanks. That gives me some things to check. What would the sensor look like? Would it be in the area where the unit is located? I will have to look at the PDF on my work computer. I really apricate your input on this matter. I will be back at the boat next weekend.


About the marine-ac.com Forum

Forum Timezone: America/New_York

Most Users Ever Online: 29

Currently Online:
18 Guests

Currently Browsing this Topic:
1 Guest

Forum Stats:

Groups: 5
Forums: 11
Topics: 398
Posts: 2369

Membership:

There are 336 Members
There have been 143 Guests

There are 2 Admins
There is 1 Moderator

Top Posters:

GeorgeH – 47
Angela – 45
z28jimi – 25
MexicoMike – 21
reefgeorge – 21
ThirdHatt – 18
Mr. Dee – 17
davidwigler – 17
biohazard – 17
mixman – 16
Ultimate Indulgence – 15
CaptainYAH – 14

Recent New Members: rudy1k, becsvet, adjustrite, blackwatch30, DWB, Raymond, pbrads1021, sizematters, cgeist, TMorse, Iproff, Ernie Jones

Administrators: Steve Pooler (1127 Posts), Scott Pooler (13 Posts)

Moderators: Steve Pooler (1127 Posts)



 
Bookmark and Share