SX24C W/ SMX11 CUTS OFF WITH LO AC ON DISPLAY

Post
New Member

Lynn

N. Georgia

posts 2

6:57 pm July 7, 2011

Post edited 7:01 pm – July 7, 2011 by Lynn


Thanks Steve for the great info forum: I am an old commercial / residential contractor. Watersouce but not Marine air.

My dock neighbor has a  90' Summerset houseboat about 11 years old wtih 2 units and digital controls. One was cutting off over the weekend. When we started checking it, we had 70/260 psig, 12F subcooling and 8 SH, unit has txv. We cleaned the water strainer and head went to 255, Delta T on evap was 24 F. Unit is in crawl space under cabin. We then cleaned evap with coil cleaner (was dirty) and patched duct. Unit has 1 14x14x12" O filter grille, 3- 6" and 3- 4" flex supply ducts around the parlor. That is way too little for a low pressure system but unit has a 1/2 hp motor at 1700 rpms, so it looks like a high static set up. The boat has wooden registers on the 3- 6s (4x12) which appear to be about 75% free area. The sensor is in the ductboard return.

I think the factory installed (except wood registers) unit is under ducted resulting in high TD air side. I think it could freeze in the right situation but still do not know why it cut off on its own before getting to setpoint.

I can set it on manual fan High and it runs like craxy to setpoint at 71F. So why would it cut off in auto. I do not see any reason for pressure switches to cut it off.

What do you think?

Thanks Lynn

Admin

Steve Pooler

posts 1127

8:40 am July 8, 2011

Post edited 8:55 am – July 8, 2011 by Steve Pooler


Questions Lynn~

What brand Equipment, What Size ?…I'm not aware of any Marine AC equip that age that used TXV…They were mostly all cap tube systems with R-22… 

What Brand & Model Digital Control ?…It makes a difference in how it handles the fan.

Is the Blower belt driven with a two speed motor ?…Again goes to the control & how it handles a 2 speed motor.

If the motor is two speed…The control will need to be either a Cruisair SMX or SMXnet…The SMXII or SMXir will not operate a two speed motor (only variable, like all other brand marine digital controls of that time)

If it is SMX or SMXnet then there are settings in the programming mode to activate the second speed that I can walk you thru….But then you don't really say if it is the fan that shuts off, or the compressor, or both…

There are also de-icing modes in digitals that will cycle the compressor even if not at setpoint…How that is done depends on the brand & model control…

 

Steve~

Admin

Steve Pooler

posts 1127

10:43 am July 8, 2011

Post edited 12:43 pm – July 8, 2011 by Steve Pooler


Gee Lynn…I totally missed your title  Embarassed

 

SX24C W/ SMX11 CUTS OFF WITH LO AC ON DISPLAY

That's a two ton self contained unit with variable fan…I have only installed one of those units (it was some time ago) Still don't remember it being TXV…

 

Ok…"LO AC" is a low voltage protection…It means the voltage to the unit has been below 200 volts for more than 3 minutes, and it shuts the unit down because of that…

Check the incoming voltage to the unit with your meter (while running) to confirm the low voltage…If it's not that low we can calibrate the control to the actual voltage in the programming mode…(it's a one time calibration setting)

We can also lie to it & tell it it's higher than it actually is, but I'm sure you know how compressors hate low voltage so I wouldn''t recommend doing that…

 

Pages 14 & 15 of this PDF manual cover the programming mode of the SMXII: http://www.dometic.com/FileOrg…..ration.pdf

If you need help after reading that…I'll walk you thru it  Cool

 

That TD of 24 degrees does have me wondering (we look for 15 to 18 degrees) but your pressures, superheat & subcooling all look good to me…Seems you are picking up plenty of heat…Out of curiosity…Does it look like someone sweat in that TXV ???

They do call for a total of 140 square inches of discharge area & 240 square of return…

 

Steve~

New Member

Lynn

N. Georgia

posts 2

7:01 pm July 8, 2011

Low voltage, what dumb xxx i am. I thought it ment Lo air conditioning performance!

well i think mislead you a little, Jimmy (MY tech) and i got crossed up on txv issue and I miss understood the txv answer. It is cap tube. Also the motor is 1/2 hp with a speed controller. Jimmy stuck in the hole and i was mostly looking in taking. I am 6'2" and about 255 so there was not enough butter on the boat to get me in much less turn around and make it back out!

I certainly appreciate the knowledge transfer. I think we have a handle on it . From memory we have enough suppley grill but are short on return about 144 sq in in filter grille (gross area instead of net) . Many of those Sumersets are short on return air even with the air source heat pumps. You can usually tell by the sucking sound.

i may contact you again if there is a problem in interpreting the bulletin and i will expect to pay for your time if that is ok.

It is still a little mystery about the lock outs not continuing with the fan on manual high. We will give that eledtrical a good going over. He is on the end of the dock about 200 ft plus from the disconnedt switch with 2 50 Amp power cords.

I will let you know about outcome.

Thanks

Lynn

Admin

Steve Pooler

posts 1127

10:04 pm July 8, 2011

Lynn~

I really would like to hear the end of this story  Cool

 

Steve~


About the marine-ac.com Forum

Forum Timezone: America/New_York

Most Users Ever Online: 29

Currently Online: rudy1k
18 Guests

Currently Browsing this Topic:
1 Guest

Forum Stats:

Groups: 5
Forums: 11
Topics: 398
Posts: 2369

Membership:

There are 336 Members
There have been 143 Guests

There are 2 Admins
There is 1 Moderator

Top Posters:

GeorgeH – 47
Angela – 45
z28jimi – 25
MexicoMike – 21
reefgeorge – 21
ThirdHatt – 18
Mr. Dee – 17
davidwigler – 17
biohazard – 17
mixman – 16
Ultimate Indulgence – 15
CaptainYAH – 14

Recent New Members: rudy1k, becsvet, adjustrite, blackwatch30, DWB, Raymond, pbrads1021, sizematters, cgeist, TMorse, Iproff, Ernie Jones

Administrators: Steve Pooler (1127 Posts), Scott Pooler (13 Posts)

Moderators: Steve Pooler (1127 Posts)



 
Bookmark and Share