Overcharged

Post
New Member

nickhd64

posts 2

7:08 pm June 23, 2011

Hello this is a great location but I
am looking for some help.  I have a 16
btu unite that I believe is overcharged. I was icing up on the coil. I had a
house AC guy add some Freon to where the suction line is sweating at the top of
the compressor. Then the next problem is that the  unite started
to run for three minutes and fault out after three attempts. I changed the run capacitor
and I thought this fixed it. Know if it is cold start it will run till it
brings the temp down but then fails .. Am I over charged and compressor is
hitting liquid?

Admin

Steve Pooler

posts 1127

6:52 am June 24, 2011

When you say it ran for three minutes and faulted out after three attempts…What was the fault code on the display ?

Was a full stream of water pumping overboard ?

What brand of equipment & what brand of control ?

Self contained unit, or split system ?

Do you know what pressures the system was running ?

 

All that info will help me help you….

 

Steve~

New Member

nickhd64

posts 2

9:13 am June 24, 2011

When you say it ran for three minutes and faulted out after three attempts…What was the fault code on the display ?

Answer CLF

Was a full stream of water pumping overboard ?

Answer Yes full stream

What brand of equipment & what brand of control ?

Answer – Marine Air System Self Contained Marine Air conditioner and Heat pump model VHT16K-H.

Control board I would have to look

Self contained unit, or split system ? Self contained unit

Do you know what pressures the system was running ?

Low 48 high 148 using old gauges.

Admin

Steve Pooler

posts 1127

10:35 am June 24, 2011

nickhd64 said:

When you say it ran for three minutes and faulted out after three attempts…What was the fault code on the display ?

Answer CLF…This stands for "Compressor Load Fault"

Was a full stream of water pumping overboard ?

Answer Yes full stream

What brand of equipment & what brand of control ?

Answer – Marine Air System Self Contained Marine Air conditioner and Heat pump model VHT16K-H.…This tells me the unit was produced between 1993 & 1995 and originally came with the ECU MAXX control system…

Control board I would have to look

Self contained unit, or split system ? Self contained unit

Do you know what pressures the system was running ?

Low 48 high 148 using old gauges.…These are way too low….With R-22…Should never be lower than 58 on the suction side…Both low & high side will depend on water temp & heat load…

At 48 psi R-22 is around 25 degrees, thus will freeze the humidity that passes across the evaporator coils…You also are not getting enough refrigerant return to the compressor which will cause it to overheat.

 

Thanks for the answers Nick~

What could be happening is the compressor is getting hot & tripping the Thermal Overload on a restart (the control sees this & faults)

I would say that if you recently had the system charged & it was charged properly with the correct refrigerant (R-22) then you have a leak…That loss of refrigerant can cause any or all of the above symptoms…

Please don't run it low on refrigerant…You will loose that compressor if you haven't already…Have the leak located & repaired…

 

Steve~


About the marine-ac.com Forum

Forum Timezone: America/New_York

Most Users Ever Online: 29

Currently Online: rudy1k
10 Guests

Currently Browsing this Topic:
1 Guest

Forum Stats:

Groups: 5
Forums: 11
Topics: 398
Posts: 2369

Membership:

There are 336 Members
There have been 143 Guests

There are 2 Admins
There is 1 Moderator

Top Posters:

GeorgeH – 47
Angela – 45
z28jimi – 25
MexicoMike – 21
reefgeorge – 21
ThirdHatt – 18
Mr. Dee – 17
davidwigler – 17
biohazard – 17
mixman – 16
Ultimate Indulgence – 15
CaptainYAH – 14

Recent New Members: rudy1k, becsvet, adjustrite, blackwatch30, DWB, Raymond, pbrads1021, sizematters, cgeist, TMorse, Iproff, Ernie Jones

Administrators: Steve Pooler (1127 Posts), Scott Pooler (13 Posts)

Moderators: Steve Pooler (1127 Posts)



 
Bookmark and Share