Compressor seems to run hot during heat cycle

Post
New Member

Kev

posts 2

1:20 pm September 14, 2011

Hello Steve, first I would like to say that this has to be the single greatest resource for marine air systems on the entire web. I can only imagine the incredible effort needed to maintain the site. Sincerest thanks, with such support why would anyone buy an A/C unit anywhere else. I have what I hope is an easy question for you…… but first…

 

My system: Marine-Air VRE12KH with ECU control (1990-91) 12,000btu. An aftermarket unit not presently installed in boat, usage fresh water Great Lakes Canada. The ECU control is dead & the entire unit is currently on my work bench to test the comp/fan/evap/condenser assy to determine if it is worth upgrading the control. The unit was rarely ever used & is virtually indistinguishable from new. It has not been turned on in 10 or 12 years. At the moment I have the compressor and fan jumpered to the 120VAC line and feeding the cooling water via a garden hose.

 

My question: While in cooling mode, the compressor runs slightly & evenly warm but when I manually power the reverse solenoid to switch to heat mode, it does start blowing 'somewhat' warm air, the condenser gets ice cold, but I note that the compressor starts to get hot within 1 or 2 minutes. (By hot I mean uncomfortable to hold your hand on it anymore) I do not know if it will get even hotter if let run longer as I was fearful of damaging the compressor. Does this sound normal to you?

 

One other thing I noted (and may or may not be relevant) was that in cooling mode there is only a 10 degree difference between the return air and the fan outlet. (no ducts connected, measured right at the fan outlet and center of the evaporator)

 

Any thoughts?

Admin

Steve Pooler

posts 1127

1:36 pm September 14, 2011

Post edited 2:28 pm – September 14, 2011 by Steve Pooler


Hi Kev~

 

Thanks for the kind words…I often ask myself why more folks don't buy from me  Confused

 

First take a look at this link: http://dometic.com/FileOrganiz…..ors%20.pdf

Scroll down to the picture titled Replacement Compressors…Does your's look like the one on the left or right ?

Left is a piston type, Right is a Rotary type…

Rotary's get Hot, Pistons should not…But both will increase temp in the heat mode…

If it's a Rotary it's also not uncommon for them to take as much as 10 minutes to really get pumping good…This may explain your 10 degree TD…

Also are you using the Same thermometer ? (gotta compare apples to apples)…I can never find 2 thermometers that read exactly the same sitting side by side & Infra Red guns are only good at reading surface temp…They are NO good at reading air or water temp…

 

Steve~

New Member

Kev

posts 2

2:57 pm September 14, 2011

Hi Steve,  Regarding new unit sales, it's because the great wealth of info on this forum is resulting in many units being put back into operation that would……. should? otherwise be junked. Wink

 

I checked the link provided and it is the rotary style, am delighted to hear these normally run hot. Is there any sort of benchmark/generic operating temperatures on these rotary compressors? I see what appears to be a thermal switch on top of the compressor, is it safe to assume this will shut down / protect the compressor if it gets too hot operationally, (I would love to leave it in heat mode for awhile to be sure there is in fact no problem), or is this switch simply to prevent on-board camp fires. ie: too late for the compressor if it opens.

 

I obtained the 10 degree TD using a digital thermocouple meter, measuring one then the other. I will let it run longer in cool mode and see if TD increases. I think I read in another post on the forum that a low TD could be the result of low refrigerant?

Admin

Steve Pooler

posts 1127

6:15 pm September 14, 2011

Post edited 11:41 am – September 16, 2011 by Steve Pooler


Kev said:

Hi Steve,  Regarding new unit sales, it's because the great wealth of info on this forum is resulting in many units being put back into operation that would……. should? otherwise be junked. Wink

Well yes…We do try to give the DIY guy/gal some options….

 

I checked the link provided and it is the rotary style, am delighted to hear these normally run hot. Is there any sort of benchmark/generic operating temperatures on these rotary compressors?…No…They can run very hot…The discharge gas (which is hot) is in direct contact with the compressor can in rotary's…. I see what appears to be a thermal switch on top of the compressor, is it safe to assume this will shut down / protect the compressor if it gets too hot operationally, (I would love to leave it in heat mode for awhile to be sure there is in fact no problem), or is this switch simply to prevent on-board camp fires. ie: too late for the compressor if it opens…The overload is there to protect…The compressor temp is one thing…Over Amperage of the wire is another…But please know it is the LAST protection in-line of anything…

 

I obtained the 10 degree TD using a digital thermocouple meter, measuring one then the other. I will let it run longer in cool mode and see if TD increases. I think I read in another post on the forum that a low TD could be the result of low refrigerant?…Yes it can be an indication of low refrigerant….But icing is also an indication of low refrigerant….

I can't really say much more without knowing about the pressures you are running….With the temp of the cabin, and the temp of the water at that given time…It all applies…Some of it will tell me if your duct work is insufficient (which is very common with Ocean)

 

Steve~


About the marine-ac.com Forum

Forum Timezone: America/New_York

Most Users Ever Online: 29

Currently Online:
8 Guests

Currently Browsing this Topic:
1 Guest

Forum Stats:

Groups: 5
Forums: 11
Topics: 398
Posts: 2369

Membership:

There are 334 Members
There have been 143 Guests

There are 2 Admins
There is 1 Moderator

Top Posters:

GeorgeH – 47
Angela – 45
z28jimi – 25
MexicoMike – 21
reefgeorge – 21
ThirdHatt – 18
davidwigler – 17
Mr. Dee – 17
biohazard – 17
mixman – 16
Ultimate Indulgence – 15
sabrejocky – 14

Recent New Members: becsvet, adjustrite, blackwatch30, DWB, Raymond, pbrads1021, sizematters, cgeist, TMorse, Iproff, Ernie Jones, Holsum69

Administrators: Steve Pooler (1127 Posts), Scott Pooler (13 Posts)

Moderators: Steve Pooler (1127 Posts)



 
Bookmark and Share