Compressor and Water pump wont turn on

Post
Member

biohazard

posts 17

2:51 am July 30, 2011

Post edited 9:49 am – July 30, 2011 by biohazard


Hi steve I am back again.  I have a marine air vcp 10k

 

I noticed today my a/c unit stopped working again.  It would make a loud click noise, but no response from the compressor or pump.  I found the sound to come from the control box and a switch or relay of some sort below the control box with a couple wires coming off it.  

 

I tested power at my pump and realized I had no power.  I saw a similar post so I opened the control box, tested power there, had 120 coming in the L1 and L2 lines.  I tested the power in the control box when turning the unit on at the comp L1 and comp L2 lines, no power.  Same result for the pump L1 and L2 lines.  As far as I can tell the compressor and pump are never being given power.  The fan however does get power after about 15 seconds.  

 

Of course it has to fail in 80% humidity at 1am.  Anything you can help me with to test what is going on with this unit now?  Is there a way to bypass that relay or whatever it is down there?

Admin

Steve Pooler

posts 1127

7:21 am July 30, 2011

Post edited 7:29 am – July 30, 2011 by Steve Pooler


biohazard said:

Hi steve I am back again.  I have a marine air vcp 10k

 

I noticed today my a/c unit stopped working again.  It would make a loud click noise, but no response from the compressor or pump.  I found the sound to come from the control box and a switch or relay of some sort below the control box with a couple wires coming off it.…From your description it seems you are describing the Reversing Valve…It's normal for it to click before a start…It does this to equalize system pressures so that the compressor does not try to start against high head pressure…This likely indicates that the control is asking for compressor…  

 

I tested power at my pump and realized I had no power.  I saw a similar post so I opened the control box, tested power there, had 120 coming in the L1 and L2 lines.  I tested the power in the control box when turning the unit on at the comp L1 and comp L2 lines, no power.  Same result for the pump L1 and L2 lines.  As far as I can tell the compressor and pump are never being given power.  The fan however does get power after about 15 seconds.…Fan after 15 seconds sounds about right…But the relays for the compressor & pump are not closing…You might try tapping on them with the plastic handle side of a screwdriver (little black boxes near the center of the board)…If this works you know your board is on it's way out…  

 

Of course it has to fail in 80% humidity at 1am.  Anything you can help me with to test what is going on with this unit now?  Is there a way to bypass that relay or whatever it is down there?

 

I show the VCP units as being from 1998 with Passport II controls…The board for that control is still available (keypad/display is not) but it is priced at $5 more than a complete retrofit to the present Passport I/O system that has many improvements over the Passport II…

 

With your past issue/s…You may also want to consider a complete new unit…The new Turbo units will outperform that unit in every way…http://www.dometic.com/enus/Am…..taid=84881

 

BTW…I just went back over your other thread…I was wrong about your ductwork size….I guess somehow I got to thinking you had a 16K and not a 10K…10K is ok with 6" duct…It's a 16K that needs the 7"…..

Sorry for the mixup  Embarassed

 

Steve~

Member

biohazard

posts 17

10:40 am July 30, 2011

Well I pulled the board out and sure enough one of the connections on the relay is burned to the board.  $2500 is a bit out of my budget for a new a/c unit though I would like to have one.  I cant belive a $3 part takes down an entire a/c unit.  How much are we looking at for this board ?  Do you know anyone that might have a old one around?

 

I a tryin to find relays but these seem to be special made for this unit.  Do you know anywhere to find them?

Member

biohazard

posts 17

11:15 am July 30, 2011

Post edited 11:34 am – July 30, 2011 by biohazard


Well here are a couple pics, I got the relay out.  Is it normal to always have a soldering iron onboard? :) I think I MAY have found one.  Is there any datasheets on the wiring so I can confirm the one I found is ok?

Here is what I found, looks identicle, power seems to be ok except that one is 28vdc and mine is 14vdc

http://www.jameco.com/webapp/w….._145753_-1

 

http://i405.photobucket.com/albums/pp133/bionetworks/IMG_20110730_094758.jpg

 

http://i405.photobucket.com/albums/pp133/bionetworks/IMG_20110730_094750.jpg

Admin

Steve Pooler

posts 1127

11:22 am July 30, 2011

The board for the Passport II retails for $570.00 with no return on electrical parts…So look at this PDF to be sure it is actually what you have http://marine-ac.com/marine-ac…..ion-units/ click on it to change pages & match up your board to be sure…

Still say…You are much better off getting the retrofit kit to the Passport I/O which comes with the Board, Display/Keypad, 15' cable, 7' temp sensor, and quick reference card for $565.00…It covers all the bases for $5 less…

Why replace old technology with the same when improvements have been made…If your display fails there are no replacements for it & it will not talk to any other board…

You also will already have the keypad/display for a new Turbo unit if needed later…

I have no other source for the relay alone…Sorry  Frown

I do discount the retrofit but can't quote here…Send me a mail to service@marine-ac.com and I can quote there.

 

Steve~

Admin

Steve Pooler

posts 1127

11:28 am July 30, 2011

biohazard said:

Well here are a couple pics, I got the relay out.  Is it normal to always have a soldering iron onboard? :) I think I MAY have found one.  Is there any datasheets on the wiring so I can confirm the one I found is ok?

Here is what I found, looks identicle, power seems to be ok except that one is 28vdc and mine is 14vdc

http://www.jameco.com/webapp/w….._145753_-1

 

http://i405.photobucket.com/albums/pp133/bionetworks/IMG_20110730_094758.jpg

 

http://i405.photobucket.com/albums/pp133/bionetworks/IMG_20110730_094750.jpg

Sorry I can't be of much help there…Marine Air gives us no specs or info on individual board parts & the failure could also be from some other component down the line…Likely one of the reasons why they came out with a new model…

 

Steve~

Member

biohazard

posts 17

11:49 am July 30, 2011

Post edited 12:05 pm – July 30, 2011 by biohazard


the board doesnt look like any on the list bu similar to the passport 2.  Do you think anything on the unit itself could have caused this to happen like a locked compressor or something or is this for sure the board?

I sent you an email

 

http://i405.photobucket.com/albums/pp133/bionetworks/IMG_20110730_104141.jpg

Admin

Steve Pooler

posts 1127

12:46 pm July 30, 2011

That's a good point…I would connect the compressor, fan & pump wires together, then apply power…If it trips a breaker, then remove one component at a time & retest each time…

The reason I say to do it that way is if all run together you can also verify that the unit still cools ok…

I'll answer your mail now.

 

Steve~

Member

biohazard

posts 17

1:31 pm July 30, 2011

Do you mean just tie them all straight together form the main power coming in??  Thus bypassing the board all together?

Admin

Steve Pooler

posts 1127

1:43 pm July 30, 2011

biohazard said:

Do you mean just tie them all straight together form the main power coming in??  Thus bypassing the board all together?

Yes…All L1's with L1…And All L2's with L2 (which is actually neutral)

If it all runs you can turn it on & off with the breaker but you obviously won't have a thermostat control.

 

Steve~


About the marine-ac.com Forum

Forum Timezone: America/New_York

Most Users Ever Online: 29

Currently Online:
8 Guests

Currently Browsing this Topic:
1 Guest

Forum Stats:

Groups: 5
Forums: 11
Topics: 398
Posts: 2369

Membership:

There are 334 Members
There have been 143 Guests

There are 2 Admins
There is 1 Moderator

Top Posters:

GeorgeH – 47
Angela – 45
z28jimi – 25
MexicoMike – 21
reefgeorge – 21
ThirdHatt – 18
davidwigler – 17
Mr. Dee – 17
biohazard – 17
mixman – 16
Ultimate Indulgence – 15
sabrejocky – 14

Recent New Members: becsvet, adjustrite, blackwatch30, DWB, Raymond, pbrads1021, sizematters, cgeist, TMorse, Iproff, Ernie Jones, Holsum69

Administrators: Steve Pooler (1127 Posts), Scott Pooler (13 Posts)

Moderators: Steve Pooler (1127 Posts)



 
Bookmark and Share