Air Handlers: 18k btu w/600cfm or 24k btu w/480cfm?

Post
Member

ThirdHatt

Madisonville, LA

posts 18

7:49 pm January 10, 2012

Oh Steve, I'm sorry! I thought that was exactly what you were after! You told me not to change any of the settings yet so I certainly didn't want to go pressing buttons without your expert guidance. I looked at the displays and other than "A34" on startup to identify the board all they displayed was return temps and supply temps. Are those return and supply temps not the same as inlet and outlet temps? Should I be scrolling through a menu to get inlet and outlet? If so, please tell me exactly what you want me to do.

 

THANKS!

Admin

Steve Pooler

posts 1127

9:34 pm January 10, 2012

I do want supply & return temps before we go anywhere (yes the 150 reading is a problem)

For now…Forget what I said about buttons or anything else…(including the above)

I just want to know what each chiller flashes back & forth while it is running…

Thanks…

 

Steve~

Member

ThirdHatt

Madisonville, LA

posts 18

11:26 pm January 10, 2012

Okay, no problem Steve. The supply and return temps are just as I posted above. That is exactly what each chiller flashes back and forth while they are running and what I thought you had asked me to get for you. To clarify, the #1 Chiller is set to turn on at 42 degrees and off at 50 degrees (seems about normal?), and the #2 chiller is also set to turn on at 50 degrees (but always displays "sup 150") and set to turn off at 48 degrees. When they are both powered up and running together they turn on at the same time and turn off at the same time even though the displayed temps are not the same between the two.

What is particulary confusing to me is that the #2 chiller is set to turn off at 48 degrees and the #1 is set to turn off at 42 degrees but yet they both cycle together whenever they are both powered up. Also, they both power on at the same time (apparently at 50 degrees) but although the #1 chiller actually displays 50 degrees when the #2 chiller still displays 150.

Hopefully this will help in your diagnosis.

Admin

Steve Pooler

posts 1127

9:10 am January 11, 2012

Byron~

What you are seeing is not what you think…Those are not setpoints…They are the actual temps of the water leaving & returning after being heated by the air coils & that's what I wanted to know…You confused me when you described on & off temps  Embarassed

Seems the one chiller does have a bad sensor (talk about that later)…But going by the other with 42 outlet & 50 return tells us we have a 8 degree loop TD (temp differential)

8 degree TD is a bit high…We are actually better off with a 5 or 6 degree loop TD.

High loop TD can mean lack of water flow, or air in the loop system…This is one of the "Most Important" things in a chiller system…Lack of flow or air, can cause frozen spots in the chillers plate coil & thus cause a rupture that would cause a loss of the refrigerant, and then fill the refrigerant system (and the compressor) with chiller loop water…Chillers are not cheap !!! and when this happens they are done….

I'm not saying this has happened, but you need to be aware of how important it is, and that it is something that needs to be monitored/checked often…Yes the chillers have protections for flow & freeze up but they are not always 100% effective.

  • When was the last time the loop was filled ?
  • Do you know where the loop pressure gauge, pressure regulator & fill valve are ?
  • If so…What is the loop pressure ? (As I mentioned earlier should be 15 to 18 psi)
  • Does the loop have automatic air bleeders ?
  • If not…When was the last time it was bled ?
  • Do you know where the bleeders are on each air handler ?

Back to setpoints:

The benefit of lower setpoints is better humidity removal & better overall cooling performance with the colder air coils… 

One of the reasons the loop TD is important is It can effect how low we can run the loop without risk of freeze up, or freeze up shutdowns…

The freeze up shutdown is set (fixed) at 38 degrees…So to avoid tripping that protection we must keep the outlet temp above that…

Also know that setpoint differential is fixed at 2 degrees and is sensed on the return water from the air coils…So with a setpoint of 50 the chiller shuts off at 50 & comes back on at 52 (return)

Now with a 8 degree Loop TD…That means we can only set a setpoint of 50, maybe 48 degrees to avoid shutdowns (I try to set for 40 degrees out) that leaves a degree or two of safety, but still allows us to run coil temps similar to a refrigerant system & take advantage of the better humidity removal & performance that goes along with it….But remember the 2 degrees fixed setpoint differential ?…This means the chiller/s won't come back on till 50 or 52 degrees…

Now if we can get the loop TD back down to at least 6 degrees…Meaning we can lower our setpoint to 46…The chiller will come back on at 48…That's 4 degrees lower than the above example, and when staging two chillers the secondary chiller could be set at either 47 or 48 thus the loop is never above 50…

To read your Cooling setpoint…Depress & Release the upper of the two buttons until the display reads CSP…It will then switch to display the actual setpoint for a few seconds…Then it will automatically revert back to the alternating loop temps.

Hope all that makes sense & BTW…DX systems (Direct Expansion or Refrigerant) are designed to run 36 to 42 degree evaporators (air coils)

 

Steve~

Member

ThirdHatt

Madisonville, LA

posts 18

9:56 am January 11, 2012

Sorry about the confusion in how I described what I was seeing! Being a lay person with limited knowledge with CW systems, I am not up on the proper terminology and apparently I am having some difficulty in providing you with what you ask for.

Let me try to answer your questions:

I top off the loop whenever I see the pressure guage drop much below 15psi. I usually catch it when it gets to 12-13 and almost always before it gets below 10, but not always. I realize there is a slow leak somewhere in the loop but from what I understand most (especially older) CW systems have some sort of a leak and they can be a real bear to find because small leaks can look exactly like condensation on the lines, etc. I do not have to add water very often, maybe twice a month in the summer whent he system is running constantly.

I do not know if the loop has automatic air bleeders, but I would suspect that it does not. I have owned the boat for exactly two years this week and I do not have any knowledge of the system being bled. I would assume not since the new chillers were installed in 2008 because the boat hit the market for sale shortly thereafter and was not in use until I bought it.

I have seen the little clear tubing with the brass end cap on several of the air handlers that are for bleeding. I remember trying to bleed one air handler one time when the water flow valve was not opening properly, but I did not get any air just a good stream of water and it turns out the CW temp sensor had slid off the tubing of the handler so it did not know when to tell the valve to open.

I agree about the setpoints. I am all ears as to what steps I should take. I should have time later today to check the CSP for you, but if not it may not be until tomorrow. Then we can move forward to make the adjustments that you recommend.

FYI, both chiller model #'s are MCW60SRCN.

Admin

Steve Pooler

posts 1127

10:27 am January 11, 2012

First thing I would do is go to the highest (elevation) air handler, find it's bleeder & with the make up water valve turned on, loop pump running & air handler calling for cooling (Valve open)…Open the bleeder & let it run for awhile…Either into it's own condensate drain pan or overboard if possible…

Then I would go back down to the chillers & check their bleeders to see if any foamy or milky water comes out…If so continue bleeding there till it runs clear…Then go back up top & check there again…Then go to each & every AH in between & check.

After that…Recheck your loop TD & see if it's lower than 8 degrees…If so, you have done a good thing for everything involved…Air in the loop will even cause premature loop pump impeller & housing failure from cavitation burns…Like a prop might get…

 

Steve~ 

Member

ThirdHatt

Madisonville, LA

posts 18

11:19 am January 16, 2012

Steve, I did as you suggested and bled the highest elevation air handler with the loop pump running, make up water on and the air handler running with valve open. I was careful to see and listen for air in the system but I did not find any. I let it run for a while and then went to check the chillers. They both bled clear of air as well, with no spitting just strong flow of clear water. I then went back tot he highest elevation chiller and it was still fine. I even bled the next two lower air handlers just to see and they were fine as well.

 

I then rechecked the loop TD and it is unchanged at 8 degrees.

Admin

Steve Pooler

posts 1127

12:31 pm January 16, 2012

Post edited 1:06 pm – January 16, 2012 by Steve Pooler


Ok Byron…If there is no air in the system…That 8 degree TD tells me you are maybe a bit shy on loop water flow…

Probably not a lot you can do about it easily at this point but it does tell me about the system…And if it were up around 10 degrees I''d be a bit more concerned…You may want to re-visit it come summer time & see if it is closer to 6 degrees then…

For now…I would set one chiller at 48 degrees & the other at 50…This should at max give a 52 degree return, and hopefully keep the out to the coils water around 40 to 42 degrees…(similar to a DX system at it's higher end)

If one chiller is enough to keep the loop below 52…The second will not come on…And if it does it will only run till the loop return is 50 degrees…

To change the CSP…Use the top button till the unit display's CSP & then temp…While the current CSP is displayed press the lower button…First touch (I forget which) either lowers CSP or raises it…Releasing the lower button & pressing again makes it go the other way…Once where you want it just leave it and the display will revert back to rotating in & out temps.

Try those above settings & see how it does..We can always widen them a degree if you feel #2 is cycling too much, or bring them down to 1 degree apart if you feel the loop is getting too warm…If you get a FRZ showing on a display, then we need to bump up a degree on both chillers…

Then go back in & tap the top button until it display's "dl"….this is time delay…The factory setting is 15 seconds, and both chillers are likely still set the same…I would raise one to start 20 seconds after the first…This might also help with breakers tripping…

 

Here is a PDF link to the DDC board manual in case you want to know what the rest of the settings do (Pg 7)

http://www.dometic.com/FileOrg…..81-DDC.pdf

We also need to get you a new temp sensor for the one reading 150…That chiller won't heat until we do…

If you still feel you need a new larger AH…I'm happy to help there too  Cool

 

Steve~

Admin

Steve Pooler

posts 1127

9:55 am January 17, 2012

Byron~

Forgot to mention & Don't know why  Embarassed….But It may be time to check your loop's "Y" strainer…It's had enough time to catch all of or most of any installation junk that may have been out in the system…If partially plugged it would explain the Higher TD…

Can't tell you where they may have installed it except it's usually near the chillers…It should be insulated and will have a pipe plug you remove to access the screen…If they were smart at installation, they would have installed isolation valves so that you don't loose loop water to clean it…

 

Steve~


About the marine-ac.com Forum

Forum Timezone: America/New_York

Most Users Ever Online: 29

Currently Online:
8 Guests

Currently Browsing this Topic:
3 Guests

Forum Stats:

Groups: 5
Forums: 11
Topics: 398
Posts: 2369

Membership:

There are 334 Members
There have been 143 Guests

There are 2 Admins
There is 1 Moderator

Top Posters:

GeorgeH – 47
Angela – 45
z28jimi – 25
MexicoMike – 21
reefgeorge – 21
ThirdHatt – 18
davidwigler – 17
Mr. Dee – 17
biohazard – 17
mixman – 16
Ultimate Indulgence – 15
sabrejocky – 14

Recent New Members: becsvet, adjustrite, blackwatch30, DWB, Raymond, pbrads1021, sizematters, cgeist, TMorse, Iproff, Ernie Jones, Holsum69

Administrators: Steve Pooler (1127 Posts), Scott Pooler (13 Posts)

Moderators: Steve Pooler (1127 Posts)



 
Bookmark and Share